An electrical panel mounting on a door surface

xenuem

Member
Location
Rockville, MD, United States
Occupation
Fire Protection Engineer
I am wondering whether there exists a regulation within the NEC that explicitly prohibits the mounting of any electrical panel onto the surface of a door. The door in question is not associated with a building but rather forms part of a large container housing electrical equipment. The panel in question is responsible for controlling the devices contained within the container. The container is not intended for human occupancy and the panel is located on the inner side of the door so that it can be secured from outdoor environmental conditions.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Does the door open with panel mounted on the door?
Is there electrical clearance per 110.26?
A sketch would help.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Is this a panel board, with feeders and branch circuits, or an industrial control panel?
Electrical components, like pushbuttons and lights, are mounted on hinged enclosure doors all the time.
 

xenuem

Member
Location
Rockville, MD, United States
Occupation
Fire Protection Engineer
Is this a panel board, with feeders and branch circuits, or an industrial control panel?
Electrical components, like pushbuttons and lights, are mounted on hinged enclosure doors all the time.
It is a control panel with feeder cables and control cables. I have seen small devices on doors but have never seen this type of panel on doors.
 

PaulMmn

Senior Member
Location
Union, KY, USA
Occupation
EIT - Engineer in Training, Lafayette College
Could the panel be moved to what appears to be the end wall of the container? No need for flexible conduit!
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Thanks for the drawing on your post
Or turn the panel around, mount on strut, open the container door to access panel
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Raceways crossing the hinge is challenging. Some raceways like LTMC used where flexibility is required, but not like you propose.
 