As I am now addicted to the grounding post here's one for you all. I was replacine a 100 amp transfer switch an Kohler 30KW generator at Dirac building at FSU. It fed asub panel two floors up and the elevator controller. I built the new service right next to the old to eliminate down time. When I got ready to change over I had the 1200 amp main switch de-energized and tapped ABC busses. It was then that I noticed there was no neutral and no ground going to the sub panel. Only three phase conductors. The panel had several single phase circuits. I did an amp reading before I built the new service. A=14,B=23,C=18...I can only assume that the emt was carrying the unbalanced load. I glad I didn't break the emt connection while I was building or I would probably be dead. Check and re-check. Live by it.