I install a lot of equipment and nearly all our buildings are concrete block.
The best anchor for concrete block is an expanding epoxy with a screen tube. The 5/8" x 3 or longer tube goes in the hole and the epoxy expands out the back, and a stud is inserted in the epoxy after its injected.
It holds in a hollow or web equally well.
We also set anchors in solid slabs with a similar epoxy and SS studs, much cheaper than an expansion bolt--and these anchors can be set in green concrete, and will break off in shear before you pull it loose
Once you use the epoxy anchors you'll not want to use anything else.
Downside is you have to wait a bit for it to cure, 1 hour or so.
I use Hilti, others are out there, but Hilti is next day via UPS..