Annex D Example D2(b): Feeder Neutral Load Calculation

Status
Not open for further replies.

xptpcrewx

Power System Engineer
Location
Las Vegas, Nevada, USA
Occupation
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
I'm working through Annex D Example D2(b) and need help understanding why a 55% demand factor is being applied to "Two-4kVA ovens plus one 5.1-kVA cooking unit".
Clearly the 55% demand factor applies to Table 250.55, note 3. However consider that Table 250.55, note 4 states, "The branch-circuit load for a counter-mounted cooking unit and not more than two wall-mounted ovens, all supplied from a single branch circuit and located in the same room, shall be calculated by adding the nameplate rating of the individual appliances and treating this total as equivalent to ONE range."

Consider the example does not specify whether this equipment is or is not on a single branch circuit or located in the same room. The conservative approach is to apply note 4 but to get the minimum calculated load we would use note 3. Any insight on how to make sense of this is appreciated. Thanks in advance.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I'm working through Annex D Example D2(b) and need help understanding why a 55% demand factor is being applied to "Two-4kVA ovens plus one 5.1-kVA cooking unit".
Clearly the 55% demand factor applies to Table 250.55, note 3. However consider that Table 250.55, note 4 states, "The branch-circuit load for a counter-mounted cooking unit and not more than two wall-mounted ovens, all supplied from a single branch circuit and located in the same room, shall be calculated by adding the nameplate rating of the individual appliances and treating this total as equivalent to ONE range."

Consider the example does not specify whether this equipment is or is not on a single branch circuit or located in the same room. The conservative approach is to apply note 4 but to get the minimum calculated load we would use note 3. Any insight on how to make sense of this is appreciated. Thanks in advance.

The calculation being done is for a feeder load. Note 4 applies to branch circuits, not feeders.

(And the example specifies that the two ovens are on one branch circuit and the counter mounted cooking unit is on another branch circuit.)
 
Last edited:

xptpcrewx

Power System Engineer
Location
Las Vegas, Nevada, USA
Occupation
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
The calculation being done is for a feeder load. Note 4 applies to branch circuits, not feeders.

(And the example specifies that the two ovens are on one branch circuit and the counter mounted cooking unit is on another branch circuit.)

This makes sense. I missed the part about both wall-mounted ovens being on a single branch circuit. Thanks again!
 