Davebones
Senior Member
- Location
- North Of Tampa Fl
Have a Anodizing area we are relocating a rectifier in it .Nameplate shows FLA as 85 amps . According to ( 669.5 ) would the circuit feeding this have to be rated at least 107 amps ? ( 1.25 x 85 = 106.25 amps ) We are putting this out of site of the panel so I see us as having to have a 110 amp breaker feeding a 200 amp disconnect . Would this be correct way to interpret this section ?