Apologies if this is basic, for some reason I can't find a clear answer.
Scenario:
100A Main bus w 100A Main breaker, so 20A allowed to backfeed
100A load breaker in Main feeding 125A rated sub-panel
30A PV backfeed into this 125A sub
My thinking is the Main panel is still overloaded by the 30A PV in the sub because that 30A will still end up on the Main panel bus and it will be overloaded by 10A
Is this correct?
Thanks