A 208v device is powered from a 2-pole breaker (2 ungrounded conductors) and metered from ct's on each phase.
The attached meter records 2 separate power/energy for each leg as if it were a single phase 120 volt load.
The client tells me they calculate the load of this device my adding the two readings together.
My gut tells me this is suspect, unless the math happens to work out magically.
Would the meter need to be configured to use the voltage across those 2 legs?
Thanks.