Question 1: Conductor Size for a 400A Feeder Tap
For a feeder tap, the conductor size must be rated to carry the current. In this case, if you are tapping off the load side of a 1200A main breaker, and dividing it by three (1200A / 3 = 400A), the conductors must be sized to handle 400A.
According to NEC 2020, section 240.21(B)(2), the ampacity of the tap conductors more than 10 feet but not greater than 25 feet in length must be at least one-third of the rating of the overcurrent device protecting the feeder conductors. This implies the conductors should be rated for at least 400A in this scenario.
Question 2: Feeder Tap Landing Sequence
The sequence of connecting the feeder tap to the overcurrent protection device (OCPD) and meter is crucial.
According to NEC 2020, Article 240.21(B)(2):
- The tap conductors must terminate in a single circuit breaker or a single set of fuses that limit the load to the ampacity of the tap conductors.
- The conductors must be protected from physical damage by being enclosed in a raceway or by other approved means.
Thus, the feeder tap conductors should first land in an OCPD before proceeding to the meter to comply with the requirement that tap conductors must terminate in a protective device that limits the load to the ampacity of the tap conductors.
However, local service provider guidelines, like those from CenterPoint Energy and Oncor, may have additional or different requirements about meter mounting and sequencing. These guidelines indicate that typically, the meter should be installed before the service equipment (including OCPD).
Summary
- Conductor Size: The conductors for a 400A tap should be rated for 400A.
- Sequence: The feeder tap should first land in an OCPD before the meter to comply with NEC 2020.