Another another generator questions thread

Status
Not open for further replies.

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
For a residential stationary generator, what is the distance requirement to the nearest operable window or door, and how is that measurement made? Is it along the wall, along a straight line nearest corner to corner, etc?
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
I think Generac recommends 5' measured from any point on the generator to the corner of the window. However, I've had situations where that wasn't feasible. So, rather than installing the generator parallel to the house I turned it 90 degrees and faced the exhaust away from the house. Got approval from the EI before I did it though.
 

kec

Senior Member
Location
CT
Occupation
Electrical Contractor
Also be careful of Dryer vents, intakes. Around here its 10'
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
So far, I'm seeing 18" from house and 5' from openings. If there is a foundation vent within, should it be sealed?
 