I've read a number of posts on box calculations and seen opinions on other sites, yet it's still not clear to me. I deal with residential construction utilizing circuits for switch boxes going to fixtures, etc.
For example: a switch box on a 3-way circuit that feeds another branch
14-2 enters the box as the supply
14-3 exits as 3-way circuit
14-2 exits to feed the other branch
2 internal cable clamps utilized (top & btm)
1 3-way switch
I understand the code as:
14-2 3 conductors (w/ground)
14-3 4 conductors (w/ground)
2 clamps 2 conductors
1 switch 1 conductor
TOTAL 13 conductors or 26 cubic inches (2 cubic inches for each 14 gage conductor)
I've also seen interpretations as all grounds counting as 1 conductor total, yielding 11 conductors or 22 cubic inches. And opinions that the switch should count as 2.
Which is right? Am I missing something else?
Also, if only the supply was 12-2 would all conductors be calculated as 12 gage or would just the supply be calculated as 12 and the rest 14?
Thanks for the clarification!
[ December 29, 2004, 02:40 AM: Message edited by: syakoban ]
1 3-way switch