I appreciate any help in interpreting 430 for multiple motors that run simultaneously. I have:
1. Motor #1 - 8.5HP on 460v/3p, with FLA of 18.6A and LRA of 125A
2. Motors #2 and #3 - connected on L1 and L2 of the 3p conductor, with FLA = 1.9A each
I want to verify size of the common OCPD. I read at a disconnect vendor site that I would need to "add together one equivalent full-load current and one equivalent locked-rotor current". This would put the disconnect at over 125A.
1. I don't see the "adding LRC" requirement in the code (430.52). Is this requirement correct?
2. Also, should motors #2 and #3 be handled differently?
Thanks in advance for any guidance or input.