I am looking at another Chiller feeder calculation and wanted to make sure that I am on the right track as I get familiar with Chiller calculations.
A new 480V 1200A Switchboard is being provided which will feed a 235kW chiller along with some small auxiliary pumps that will support the chiller system. There will be a feeder breaker in the Switchboard to feed the Chiller directly and there will be another feeder breaker which will feed a small MCC which contain the small pump starters.
The Chiller schedule from the manufacturer shows the chiller as having an "MCA" of 530.6A, a "MOCP" of 700A and an "IF" of 2028.6A. It also lists a "IPLV/EER" of 12.29/10.08. I'm not sure what the "IF" and "ILPV/EER" are?
In terms of the feeder calculation for this chiller do I simply use the 700 listed OCPD to size the feeder breaker at 700A and have (2) sets of 500MCM cables for the feeder? I'm assuming that the listed MOCPD and MCA already factor in the requirements of 440.22 and 440.33 and thus there are no further multiplying factors needed for these (the manufacturer already did these calcs for us)
In terms of the load calculation for the switchboard would I simply use the MCA (530.6A) value for the chiller load or do I need to add any adjustment factors to this for the load calc.
There will be four small 10hp pumps connected to a small MCC which if fed from the switchboard. For the load calcs for these pumps I simply use 4 x 14A (FLA) plus 25% of 14A (largest FLA) to come up with 59.5A. I then add this 59.5A to the 530.6A chiller value above to come up with the total Switchboard calculated load. Am I on the right track here?
A new 480V 1200A Switchboard is being provided which will feed a 235kW chiller along with some small auxiliary pumps that will support the chiller system. There will be a feeder breaker in the Switchboard to feed the Chiller directly and there will be another feeder breaker which will feed a small MCC which contain the small pump starters.
The Chiller schedule from the manufacturer shows the chiller as having an "MCA" of 530.6A, a "MOCP" of 700A and an "IF" of 2028.6A. It also lists a "IPLV/EER" of 12.29/10.08. I'm not sure what the "IF" and "ILPV/EER" are?
In terms of the feeder calculation for this chiller do I simply use the 700 listed OCPD to size the feeder breaker at 700A and have (2) sets of 500MCM cables for the feeder? I'm assuming that the listed MOCPD and MCA already factor in the requirements of 440.22 and 440.33 and thus there are no further multiplying factors needed for these (the manufacturer already did these calcs for us)
In terms of the load calculation for the switchboard would I simply use the MCA (530.6A) value for the chiller load or do I need to add any adjustment factors to this for the load calc.
There will be four small 10hp pumps connected to a small MCC which if fed from the switchboard. For the load calcs for these pumps I simply use 4 x 14A (FLA) plus 25% of 14A (largest FLA) to come up with 59.5A. I then add this 59.5A to the 530.6A chiller value above to come up with the total Switchboard calculated load. Am I on the right track here?