1ab1
Member
- Location
- Los Angeles
- Occupation
- Developer / Contractor
SFR, Los Angeles. Owner wanted an 8-unit Mitsubishi mini split system. Inspector insisting on a disconnect for each interior unit, despite the electrician offering a lockable disconnect on the outdoor unit which powers all of the indoor units (indoor units are that 3 conductor 110V system that carries power and data from the outdoor unit). We also offered to install the disconnects in the ceiling cavity adjacent to the indoor units (ceiling cassettes) so that they are visible once you remove the grille cover. Removing the grille cover is cosmetic, the electrical connections and insides of the unit are still inaccessible without removing further cover plates from the actual unit. Electrician went back to inspector with "440.14 Location. Disconnecting means shall be located within sight from, and readily accessible from, the air-conditioning or refrigerating equipment. The disconnecting means shall be permitted to be installed on or within the air-conditioning or refrigerating equipment" but he is saying that "from his training" we cannot locate the disconnect the way we are proposing. Curious what the group's consensus is. From what we can tell LADBS has not issued a bulletin around this, as other jurisdictions have.