I am trying to get to the bottom of whether or not my existing electrical setup is a code violation and/or fire hazard. The folks I have consulted so far have been unable to convince me that there is in fact an issue and it largely seems to stem from a misunderstanding of feeder taps.
I have 200A service coming into a main panel. At the bottom of the main panel there are a set of pass-through lugs. These pass-through lugs are feeding a 125A sub-panel which is used for the HVAC. On this 125A panel there are 2x25A breakers which again are purely used for the HVAC system. The wire being used to connect the 125A sub-panel via the pass-through lugs are 2AWG rated for 100A. The distance between the main panel and the sub-panel is about 15ft and is enclosed in a protected raceway. I am being told that this is a code violation and a fire hazard as the wires are being fed 200A service and could create an overcurrent situation.
I believe my configuration would fall under Feeder tap rules. The updated 2020 NEC handbook has added language in 240.21(B) which now allows a feeder tap to be made directly to a lug or terminal. Since the distance of the conductor is greater than 10FT but less than 25FT then I would think per 240.21(2)(1) The wire would need to be rated for at least 200/3 = 66.67A. I believe my configuration also satisfies 240.21(2)(2) & 240.21(2)(3) -
(2) The tap conductors terminate in a single circuit breaker or a
single set of fuses that limit the load to the ampacity of the
tap conductors.
(This is the 125A sub-panel w/ 2x25A breakers ahead of the HVAC units)
(3) The tap conductors are protected from physical damage
by being enclosed in an approved raceway or by other
approved means
(The wire from the main panel to the sub-panel is in enclosed in a PVC raceway)
Both opinions are coming from folks at big box home service brands and have not been able to explain to me why my setup is incorrect, other than 200A into 100A = fire hazard. Hoping I could get a another opinion from this forum.
Main Panel
Sub-Panel
Thanks!
I am trying to get to the bottom of whether or not my existing electrical setup is a code violation and/or fire hazard. The folks I have consulted so far have been unable to convince me that there is in fact an issue and it largely seems to stem from a misunderstanding of feeder taps.
I have 200A service coming into a main panel. At the bottom of the main panel there are a set of pass-through lugs. These pass-through lugs are feeding a 125A sub-panel which is used for the HVAC. On this 125A panel there are 2x25A breakers which again are purely used for the HVAC system. The wire being used to connect the 125A sub-panel via the pass-through lugs are 2AWG rated for 100A. The distance between the main panel and the sub-panel is about 15ft and is enclosed in a protected raceway. I am being told that this is a code violation and a fire hazard as the wires are being fed 200A service and could create an overcurrent situation.
I believe my configuration would fall under Feeder tap rules. The updated 2020 NEC handbook has added language in 240.21(B) which now allows a feeder tap to be made directly to a lug or terminal. Since the distance of the conductor is greater than 10FT but less than 25FT then I would think per 240.21(2)(1) The wire would need to be rated for at least 200/3 = 66.67A. I believe my configuration also satisfies 240.21(2)(2) & 240.21(2)(3) -
(2) The tap conductors terminate in a single circuit breaker or a
single set of fuses that limit the load to the ampacity of the
tap conductors.
(This is the 125A sub-panel w/ 2x25A breakers ahead of the HVAC units)
(3) The tap conductors are protected from physical damage
by being enclosed in an approved raceway or by other
approved means
(The wire from the main panel to the sub-panel is in enclosed in a PVC raceway)
Both opinions are coming from folks at big box home service brands and have not been able to explain to me why my setup is incorrect, other than 200A into 100A = fire hazard. Hoping I could get a another opinion from this forum.
Main Panel
Sub-Panel
Thanks!