Ok I did a search and could not find my issue, so I had to post, 99% I can find what I need with a search but no luck today.
So this is I what I have.
To make a long story longer this is what going on.
The project is a brand new church.
The fire pump is a 60hp, 480/3V, 518LRA submersible irrigation pump that some well driller put in that?s not rated for fire pump use. Don?t ask how they got this past but they did.
In the original design we had a fire rated fire pump and fire pump controller/service rated disconnect with the fire pump controller being fed from the CT can, perfect just like it should be.
Now, the controller that the pump guy is supplying is not rated for fire use (695.10) and does not have a service disconnect. So be it I guess, I will make a letter about this to cover my a$$.
So this is what I would like to do. Use a 600amp CT can/main fused disconnect (695.4(b)(1)) with 4/0 feeders (695.6(c)(1)). I want to do my part up to code no matter what everybody else is doing.
My question is, being that I don?t have a listed fire pump controller will I have an issue with the 4/0cu conductors while using the 600amp main? I don?t see why but that?s why I'm here.
What type of fuses would we use?
Thanks
All
Jay
So this is I what I have.
To make a long story longer this is what going on.
The project is a brand new church.
The fire pump is a 60hp, 480/3V, 518LRA submersible irrigation pump that some well driller put in that?s not rated for fire pump use. Don?t ask how they got this past but they did.
In the original design we had a fire rated fire pump and fire pump controller/service rated disconnect with the fire pump controller being fed from the CT can, perfect just like it should be.
Now, the controller that the pump guy is supplying is not rated for fire use (695.10) and does not have a service disconnect. So be it I guess, I will make a letter about this to cover my a$$.
So this is what I would like to do. Use a 600amp CT can/main fused disconnect (695.4(b)(1)) with 4/0 feeders (695.6(c)(1)). I want to do my part up to code no matter what everybody else is doing.
My question is, being that I don?t have a listed fire pump controller will I have an issue with the 4/0cu conductors while using the 600amp main? I don?t see why but that?s why I'm here.
What type of fuses would we use?
Thanks
All
Jay