Another fundamental grounding/bonding question.

Merry Christmas

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
We have a 480V switchgear feeding a MCC (MCB) with a 3/C 500kCMIL plus ground.
The SWGR has a GEC that is routed from the SWGR grd bus to a ground rod/test well just outside the building.
Does the MCC ground bus also need to be bonded directly to a grounding electrode or does the feeder with an EGC from the SWGR ground bus accomplish this?


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This feeder doesn't require a direct connection to the GES. As stated the EGC has taken care of the grounding and bonding of the MCC.
 