About six years ago I installed a 10kW fixed mounted non-SDS generator and a 10 position transfer switch. The system was installed to code at the time and all manufacturing installation instructions were followed to the letter.
One of the manufacturer's installation requirements was to sink a grounding electrode at the generator location and to bond it to the ground lug at the back of the generator. Since the generator location was near the main service entrance grounding electrode, I just dug a trench and bonded the generator lug directly to the main grounding electrode. So far so good or so I thought.
Now the manufacturer has stopped recommending bonding a non-SDS generator to a grounding electrode. Probably in no small part due to Mike Holt's mission to inform everyone of the dangers of this procedure due to voltage rise issues during high voltage events between unbonded ground rods.
So my question is since I do not have a separate unbonded rod is there any harm in having the generator bonded directly to the system grounding electrode? Have I created a ground loop? Should I just disconnect the bonding jumper?
One of the manufacturer's installation requirements was to sink a grounding electrode at the generator location and to bond it to the ground lug at the back of the generator. Since the generator location was near the main service entrance grounding electrode, I just dug a trench and bonded the generator lug directly to the main grounding electrode. So far so good or so I thought.
Now the manufacturer has stopped recommending bonding a non-SDS generator to a grounding electrode. Probably in no small part due to Mike Holt's mission to inform everyone of the dangers of this procedure due to voltage rise issues during high voltage events between unbonded ground rods.
So my question is since I do not have a separate unbonded rod is there any harm in having the generator bonded directly to the system grounding electrode? Have I created a ground loop? Should I just disconnect the bonding jumper?