another generatory query

Status
Not open for further replies.

Hendrix

Senior Member
Location
New England
Meter and 200a disco on pedestal. Feeders hit service rated automatic transfer switch w/200amp breaker as soon as they enter building. Then to sub panel for branch circuit dist. Does anyone see anything wrong with this installation?
 
I might add that since you are installing a service rated switch in a feeder to make sure you don't have main bonding jumper in the ATS.
 