I have seen a number corner grounded systems, and all but one had 3 pole breakers. The one that didn't had fuses and was originally an ungrounded system. They grounded B phase at the transformer and installed dummy fuses for B phase at all of the fused disconnects.I’m sorry if I was misleading. You are 100% technically correct.
But for troubleshooting it creates more trouble than it’s worth.
Like I stated earlier, it seems like every one we have built over the last 30 years we have had to send service guys to because someone didn’t understand what they were dealing with.
Those with two fuses (legal) or two poles didn't cause as much confusion as those with three pole breakers (also legal as you stated)