I have a 100VAC device protected with a 10A class CC fuse.
NFPA 79 Table 8.2.2.3 states that for circuits not exceeding 10A a 16AWG (AWG or kcmil) wire is required.
Also, the control box has an 80A breaker. Does this mean the door and baseplate bonding wires need to be 8AWG?
Is there any justification for using wire sizes other than those listed?
Thank you.
NFPA 79 Table 8.2.2.3 states that for circuits not exceeding 10A a 16AWG (AWG or kcmil) wire is required.
Also, the control box has an 80A breaker. Does this mean the door and baseplate bonding wires need to be 8AWG?
Is there any justification for using wire sizes other than those listed?