406.4(D)(2)
(b) A non—grounding—type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles or their cover plates shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter—type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.
(c) A non—grounding—type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Where grounding-type receptacles are supplied through the ground-fault circuit interrupter, grounding-type receptacles or their cover plates shall be marked “GFCI Protected” and “No Equipment Ground,” visible after installation. An equipment grounding conductor shall not be connected between the grounding-type receptacles.
Informational Note No. 1: Some equipment or appliance manufacturers require that the branch circuit to the equipment or appliance includes an equipment grounding conductor.
Informational Note No. 2: See 250.114 for a list of a cord-and-
plug-connected equipment or appliances that require an equipment grounding conductor.
250.114 Equipment Connected by Cord and Plug. Exposed, normally non—current—carrying metal parts of cord-and—plug—connected equipment shall be connected to the equipment grounding conductor under any of the following conditions:
c. Hand-held motor-operated tools, stationary and fixed motor-operated tools, and light industrial motor-operated tools
d. Motor-operated appliances of the following types:
hedge clippers, lawn mowers, snow blowers, and wet scrubbers
This is a partial list of the things listed in 250.114, and only select wording. Read the whole thing!!!
I surmise that is impossible to install a receptacle per 406.4(D)(2)(b) without potentially violating 250.114, so why do they even have 406. When someone gets electrocuted because a contractor complied with 406, a good lawyer should sue per 250.114.
(b) A non—grounding—type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles or their cover plates shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter—type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.
(c) A non—grounding—type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Where grounding-type receptacles are supplied through the ground-fault circuit interrupter, grounding-type receptacles or their cover plates shall be marked “GFCI Protected” and “No Equipment Ground,” visible after installation. An equipment grounding conductor shall not be connected between the grounding-type receptacles.
Informational Note No. 1: Some equipment or appliance manufacturers require that the branch circuit to the equipment or appliance includes an equipment grounding conductor.
Informational Note No. 2: See 250.114 for a list of a cord-and-
plug-connected equipment or appliances that require an equipment grounding conductor.
250.114 Equipment Connected by Cord and Plug. Exposed, normally non—current—carrying metal parts of cord-and—plug—connected equipment shall be connected to the equipment grounding conductor under any of the following conditions:
c. Hand-held motor-operated tools, stationary and fixed motor-operated tools, and light industrial motor-operated tools
d. Motor-operated appliances of the following types:
hedge clippers, lawn mowers, snow blowers, and wet scrubbers
This is a partial list of the things listed in 250.114, and only select wording. Read the whole thing!!!
I surmise that is impossible to install a receptacle per 406.4(D)(2)(b) without potentially violating 250.114, so why do they even have 406. When someone gets electrocuted because a contractor complied with 406, a good lawyer should sue per 250.114.