Oh how I love my IR thermometer....
Today on site I was noticing that some temp lights were doing the hokey pokey, my drill sounded weird, some guys skil saw sounded weird too....
Checked voltage - didn't seem to change much - considering there were a lot of tools and two compressors going. But I had my thermometer in the same case with my meters - so for S&G I scanned around the cords - bingo! I got a temp of 250F on a CA 50 outlet on the side of one of the spider boxes - a little closer and it was too hot to touch.... Shut the site down - opened the cord and found the neutral had pulled almost out of the terminal - and the insulation was melting back...
Figure I got it not long before it lost contact completely. Lucky it didn't happen tomorrow when no electricians would be there....
Today on site I was noticing that some temp lights were doing the hokey pokey, my drill sounded weird, some guys skil saw sounded weird too....
Checked voltage - didn't seem to change much - considering there were a lot of tools and two compressors going. But I had my thermometer in the same case with my meters - so for S&G I scanned around the cords - bingo! I got a temp of 250F on a CA 50 outlet on the side of one of the spider boxes - a little closer and it was too hot to touch.... Shut the site down - opened the cord and found the neutral had pulled almost out of the terminal - and the insulation was melting back...