Hello,
I was going through GE Electric Range in the link below and interestingly for both 208 & 240V they have the same breaker rating although they have different kW for both the voltages.They mentioned 9.1kW for 208v and 12.1kW for 240V. If we do the math for the 208v then 9100/208=43.75A for which we have to use either 45A or 50A. I dont know why they specified 40A breaker ad even for thee 240V 12100/240=50.16A which we have to go to the next standard breaker size...Am i missing something for this range?
http://products.geappliances.com/appliance/gea-specs/JB450DFWW
I was going through GE Electric Range in the link below and interestingly for both 208 & 240V they have the same breaker rating although they have different kW for both the voltages.They mentioned 9.1kW for 208v and 12.1kW for 240V. If we do the math for the 208v then 9100/208=43.75A for which we have to use either 45A or 50A. I dont know why they specified 40A breaker ad even for thee 240V 12100/240=50.16A which we have to go to the next standard breaker size...Am i missing something for this range?