There are some apartments, and each apartment has a furnace with a 10KW electric heat pack.
It gets cold here, and that is really the only heat for the entire apartment.
Looking at 220.82(C), it looks like this should be calculated per #4 - 65% of the nameplate rating of electric space heating where there is less than 4 separately controlled units.
But I'm not sure about #6: 100% of the nameplate rating for electric thermal storage and other heating systems where the usual load is expected to be continuous at the full nameplate rating.
It seems like only the HVAC designer would know if it was intended to be continuous at full load.
So #4 or #6?