was called and asked about a meggering situation. Here is the info as best as I can pass it on to you. Maybe someone has had this experience and can help.
There is a 200ft conductor run, 6 sets of 600kcmil Al, Type XHHW conductors. Those conductors are terminated to lugs on a 52ft SQD-Iline bus duct.
The system is 480V-2000amps.
The electrician meggered out each phase while the XHHW conductors were terminated to the bus duct. He meggered all 6 parallel conductors for each phase at one time.
His setting for the megger was at 1000V.
His readings for A-B and B-C were 88M (the voltage of the megger actually read at 1080V).
His reading for C-A were very low (I believe under 10M), with the voltage of the megger not reaching greater than 147V
He tested the megger again on the other phases and recorded the same readings as earlier.
SQD-Iline literature states the megger results should be at approximately 52M for the 52ft run.
Does the coupling of the bus duct to the XHHW conductors cause the (what I think is a low reading for new work) 88M reading?
What do you think could be the reason for the unusual readings of A-C?
The tester is the Fluke 1507, brand new...with the batteries that come with the unit. Could it possibly be the batteries?
He is going to take a reading of the XHHW conductor, isolated from the bus duct. I asked him to at both 500V and 1000V for my own curiosity.
There is a 200ft conductor run, 6 sets of 600kcmil Al, Type XHHW conductors. Those conductors are terminated to lugs on a 52ft SQD-Iline bus duct.
The system is 480V-2000amps.
The electrician meggered out each phase while the XHHW conductors were terminated to the bus duct. He meggered all 6 parallel conductors for each phase at one time.
His setting for the megger was at 1000V.
His readings for A-B and B-C were 88M (the voltage of the megger actually read at 1080V).
His reading for C-A were very low (I believe under 10M), with the voltage of the megger not reaching greater than 147V
He tested the megger again on the other phases and recorded the same readings as earlier.
SQD-Iline literature states the megger results should be at approximately 52M for the 52ft run.
Does the coupling of the bus duct to the XHHW conductors cause the (what I think is a low reading for new work) 88M reading?
What do you think could be the reason for the unusual readings of A-C?
The tester is the Fluke 1507, brand new...with the batteries that come with the unit. Could it possibly be the batteries?
He is going to take a reading of the XHHW conductor, isolated from the bus duct. I asked him to at both 500V and 1000V for my own curiosity.