Mgarf33
Member
- Location
- Virginia Beach, Va
I am supplying an air handler in a residential garage with a 15kW aux heater on a #6 NM-B circuit. Circuit one requires 58A min amp conductor, and 60A MOCP. Circuit 2 is well below the 25A rating using #8 NM-B. I wish I could move the blower circuit to circuit 2 which would drop my min amp of circuit 1 to 50, but that would void the UL listing of the appliance.
So, this circuit passed on the original home construction, and the Min Amp of the existing equipment was 59A with a 60A MOCP. Correct me if I'm wrong, but isn't #6 NM-B only rated for 55A as a cable set? The run is ~35'-40' routed through a crawl space.
Yes, I realize the individual conductors are 90°C rated and can be used with 90° lug connections, but the cable set is only rated at 60°C. Is this different for residential applications?
So, this circuit passed on the original home construction, and the Min Amp of the existing equipment was 59A with a 60A MOCP. Correct me if I'm wrong, but isn't #6 NM-B only rated for 55A as a cable set? The run is ~35'-40' routed through a crawl space.
Yes, I realize the individual conductors are 90°C rated and can be used with 90° lug connections, but the cable set is only rated at 60°C. Is this different for residential applications?