In 334.30 NM Securing and Supporting, the commentary of my 2017 handbook says “Draping the cable over air ducts, rafters, timber’s, joists, pipes, and ceiling grid members without securing the cable with approved means is not permitted except, as allowed in 334.30(B)(1).” Another nationally recognized instructor agrees with this and says cables running perpendicular across the top of attic joists are to be stapled, but when I discuss this with electricians in my area they look at me like I’m crazy. Apparently, nobody staples on top of joists in my area, much less run protective strips. Am I missing something? I’m more of an industrial electrician, so I’m not familiar with what inspectors enforce or ignore. Is this something that inspectors just ignore? Similar issue with cables coming down studs. Many guys just jam several cables under large staples resulting in insufficient distance to the edge of the stud rather than using a cable stacker or simply running half he cables down the opposite stud. Is this just lax inspectors? I don’t think either issue is terribly critical, although a screw in a conductor was reported to have started a fire in a relatives house.... I just can’t get my head around how some things are enforced and some things are not. I expect it’s difficult for a new inspector to come into an area and change the way people have been doing things for 50 years... Sorry for the long message, but this has bothered me for a long time. Thanks