You need 6' of dedicated space above the MCC in the footprint of the MCC.
I don't see how a platform is "equipment". While it might be a good idea to leave that space open, I am not sure how you enforce it the way the code is written.110.26
(E) Dedicated Equipment Space. All switchboards, switchgear,
panelboards, and motor control centers shall be located in
dedicated spaces and protected from damage.
(1) Indoor. Indoor installations shall comply with 110.26(E)
(1)(a) through (E)(1)(d).
(a) Dedicated Electrical Space. The space equal to the width
and depth of the equipment and extending from the floor to a
height of 1.8 m (6 ft) above the equipment or to the structural
ceiling, whichever is lower, shall be dedicated to the electrical
installation. No piping, ducts, leak protection apparatus, or
other equipment foreign to the electrical installation shall be
located in this zone.
Put some walls under the "platform" to make an "electrical room" to contain the MCC and now that same platform is the structural ceiling of that room.That is not what the code requires.
The code says this:
I don't see how a platform is "equipment". While it might be a good idea to leave that space open, I am not sure how you enforce it the way the code is written.
That is not what the code requires.
The code says this:
I don't see how a platform is "equipment". While it might be a good idea to leave that space open, I am not sure how you enforce it the way the code is written.
Dictionary.com
[h=1]equipment[/h]Noun
- anything kept, furnished, or provided for a specific purpose.
That depends on where you get your definition of equipment.
Equipment. A general term, including fittings, devices, appliances,
luminaires, apparatus, machinery, and the like used as a
part of, or in connection with, an electrical installation.
110.26(E)(1) Indoor. Indoor installations shall comply with
110.26(E)(1)(a) through (E)(1)(d).
(a) Dedicated Electrical Space. The space equal to the
width and depth of the equipment and extending from the
floor to a height of 1.8 m (6 ft) above the equipment or to
the structural ceiling, whichever is lower, shall be dedicated
to the electrical installation. No piping, ducts, leak protec-
tion apparatus, or other equipment foreign to the electrical
installation shall be located in this zone.
Equipment. A general term, including fittings, devices, appli-
ances, luminaires, apparatus, machinery, and the like used as a
part of, or in connection with, an electrical installation.