HUDSON, Wis. - The death of a 6-year-old girl in a bathtub offers a sad lesson about the dangers of using electrical appliances near water, officials say.
Chelsea Joe (Princess) Helland was found with a hair dryer in the water-filled tub, and a medical examiner's report shows a high probability she died from electrocution, said interim Police Chief Eric Atkinson.
LawnGuyLandSparky said:Must've been an old hair dryer - as they've all had integral GFCIs built into their plugs for over 20 years now.
We've discussed this many times before. A GFIC does not require a path to ground to trip. They look at the hot and the neurtal currents. If they are not within a few milli-amps of each other they trip. Ground current is assumed , as if the current isn't going hot to neutral it must be going some place, namely ground. Also a fiber glass tub that did not provide a path to ground might also have prevented the tradgedy. You can hold on to an un-grounded conductor (hot) and if there is no complete path you will not be hurt.iwire said:If it had a GFCI it might not trip, it would require a path to ground for it to trip.
Fiberglass tub with a plastic plumbed house could very well be isolated from ground paths.
If it had a LCDI it would trip.
iaov said:We've discussed this many times before. A GFIC does not require a path to ground to trip.
They look at the hot and the neutral currents. If they are not within a few milli-amps of each other they trip.
iwire said:It needs a path to back to the source that is not on the circuit conductors.
Typically that is to ground.
Thats right, and the only way those currents can become un-equal is for current to flow another way back to the source.
Again, that is typically ground.
Bottom line is a two wire device dropped into an electrically isolated body of water will not trip the GFCI.
I agree with the first two sentences, but not with the third. You do need an additional path back to the source. But it need not be a wire. Current can flow from the hot conductor of the hair dryer, to the bath water (this path includes the person in the tub), through the water pipes (or even the water itself) to the point at which the water pipe is used as a grounding electrode, then via the GEC to the main panel.iwire said:It needs a path to back to the source that is not on the circuit conductors. Typically that is to ground. . . . Bottom line is a two wire device dropped into an electrically isolated body of water will not trip the GFCI.
But that would not be "an electrically isolated body of water" if current could flow from the water into piping.charlie b said:Current can flow from the hot conductor of the hair dryer, to the bath water (this path includes the person in the tub), through the water pipes (or even the water itself) to the point at which the water pipe is used as a grounding electrode, then via the GEC to the main panel.
Sorry, Larry, but I do not understand what you are trying to say. Are you agreeing with me :smile: or not ?LarryFine said:But that would not be "an electrically isolated body of water" if current could flow from the water into piping.
masterelect1 said:Apparently, there was current flow through the girls' body, hence the electrocution. I would surmise this is where the unbalance would occur and if there was a GFCI involved it would trip regardless of grounded vs. non-grounded.
charlie b said:
Sorry, Larry, but I do not understand what you are trying to say. Are you agreeing with me :smile: or not ?
masterelect1 said:Supposition: the hair dryer is using 7.2 amps and is dropped into the tub. The poor girls body takes a hit of 100 ma. The return to the gfci is 7.2 minus 100ma.
masterelect1 said:Supposition: the hair dryer is using 7.2 amps and is dropped into the tub. The poor girls body takes a hit of 100 ma. The return to the gfci is 7.2 minus 100ma. Typical GFCI's made to trip @ 5ma imbalance.
The GFCI must trip due to this imbalance of outgoing amps vs. return amps, ground reference not required.
charlie b said:Was my description of the current path not valid: Current passing through the person's body, then via the water/water pipe to the connection point of the GEC [...] Would that path not result in a GFCI trip?
charlie b said:Was my description of the current path not valid: Current passing through the person's body, then via the water/water pipe to the connection point of the GEC, then up the GEC to the N-G bond point, and thus having reached the source without passing through the appliance's grounded conductor? Would that path not result in a GFCI trip?
I was disagreeing. If the tub water was truly isolated, which would require non-metallic plumbing, etc., the only current pathway would be within the dryer itself.charlie b said:Sorry, Larry, but I do not understand what you are trying to say. Are you agreeing with me :smile: or not ?
I don't understand how we can say this. We have no idea if the piping to the tub was metallic or non-metallic. If it is non-metallic it may have enough isolation so that the GFCI does not trip.In other words, the electrocution would have been prevented with use of a properly-wired and -operational GFCI device.