Another service call today. This time to a resturant with an apartment above. Immediately I can tell this is a do it yourselfer with enough knowledge to be dangerous but I wanted to check it out anyway. The HVAC crew was installing an A/C unit on a (rubber) roof. When they ran the line set through the roof and happened to touch the EMT (A/C feeder) they got nailed. They proceeded and later when they touched the EMT and the rubber roof, they got nailed again.
Here is where I come in. With my FLUKE 179 (I am purchaseing a Simpson 260-8 ASAP), I read... EMT to refrigerant line: 59 VAC. EMT to metal roof boot of vent pipe: 73 VAC. EMT to rubber roof: anywhere from 59 VAC to 73 VAC. Keep in mind... The feeder to the A/C (8/3 NM cable in a 3/4" EMT) has never been energized.
I then go to the source... 120/208 VAC single phase 100 amp sub panel... Neutral bonded to the can... Feeder is a #2/3 SE cable (no ground)... A #10 AWG (in 1/2" EMT) is ran to the nearest water pipe and bonded to the EMT and the water pipe... (By now you can see it's a "do it yourselfer") All of my meter readings at the loadcenter are normal except when I read phase to any disconnected and isolated conductor in the A/C feeder, it reads 111 VAC (again, I am buying a analog meter soon)...
I then proceed to the Service Entrance and find the earth ground and water main are not bonded (the water main is not even connected). I bonded the two with a temp #14 and no change to my readings.
I did not personally "check" by getting shocked, so I am taking their word for it. Why am I getting voltage readings on a rubber roof. It (seems) obvious to me that it is a grounding issue, but only at the rubber roof. No one seems to get "hit" anywhere else. Help Please!!!
Here is where I come in. With my FLUKE 179 (I am purchaseing a Simpson 260-8 ASAP), I read... EMT to refrigerant line: 59 VAC. EMT to metal roof boot of vent pipe: 73 VAC. EMT to rubber roof: anywhere from 59 VAC to 73 VAC. Keep in mind... The feeder to the A/C (8/3 NM cable in a 3/4" EMT) has never been energized.
I then go to the source... 120/208 VAC single phase 100 amp sub panel... Neutral bonded to the can... Feeder is a #2/3 SE cable (no ground)... A #10 AWG (in 1/2" EMT) is ran to the nearest water pipe and bonded to the EMT and the water pipe... (By now you can see it's a "do it yourselfer") All of my meter readings at the loadcenter are normal except when I read phase to any disconnected and isolated conductor in the A/C feeder, it reads 111 VAC (again, I am buying a analog meter soon)...
I then proceed to the Service Entrance and find the earth ground and water main are not bonded (the water main is not even connected). I bonded the two with a temp #14 and no change to my readings.
I did not personally "check" by getting shocked, so I am taking their word for it. Why am I getting voltage readings on a rubber roof. It (seems) obvious to me that it is a grounding issue, but only at the rubber roof. No one seems to get "hit" anywhere else. Help Please!!!