little george
Member
Would it me allowed to enter the back side of a wall mounted sign with the branch circuit and travel through the sign enclosure or raceway and terminate on the line side of a weather proof switch mounted on the sign enclosure. 600.5(C)(2) talks about branch circuit conductors and secondary conductors in the same J-box, enclosure or pull box but the contractor is coming into the sign, passing through the sign to the line terminals of the exterior mounted switch and then coming back into the sign off the load side terminals to feed the sign Xformer.