Hello, I would like to resurrect this thread, because I am seeing similar problems with a solid state soft start on a 500 hp compressor for a freezer.
The soft start limits the starting current for the first 5 seconds to approximately 750 amps to 900 amps, but then jumps to approximately across the line starting current for about 0.5 seconds before settling down to running current, which is well below full load amps. Attached is a cycle by cycle snapshot of the RMS voltage and current during the start, as well as a couple waveform captures. I suspect maybe the motor is not up to at least 80% speed as Jraef previously noted, but has anyone come across a standard that talks about this?
The customer is not having a problem with overloads, but the customer is intermittently blowing main 3000 amps fuses that are feeding about 6 of these compressors. The individual fuses feeding each compressor are not blowing. There is the possibility of more than one compressor starting near the same time or at the same time...i.e. no interlocks.
No offense because this site is a great resource for me, but I probably need to go to the customer with something better than "I read it on Mike Holt's site.":smile:
Thanks!
The soft start limits the starting current for the first 5 seconds to approximately 750 amps to 900 amps, but then jumps to approximately across the line starting current for about 0.5 seconds before settling down to running current, which is well below full load amps. Attached is a cycle by cycle snapshot of the RMS voltage and current during the start, as well as a couple waveform captures. I suspect maybe the motor is not up to at least 80% speed as Jraef previously noted, but has anyone come across a standard that talks about this?
The customer is not having a problem with overloads, but the customer is intermittently blowing main 3000 amps fuses that are feeding about 6 of these compressors. The individual fuses feeding each compressor are not blowing. There is the possibility of more than one compressor starting near the same time or at the same time...i.e. no interlocks.
No offense because this site is a great resource for me, but I probably need to go to the customer with something better than "I read it on Mike Holt's site.":smile:
Thanks!