I would like to tap 300 Amp from 800 Amp service switch that already has other loads. My tap conductors will have to pass thru electric meter and then go to 300 Amp fused switch.
Does 240.21 B(2) (2) limit me and I have to have my conductors less than 10 feet?
(2) The tap conductors terminate in a single circuit breaker
or a single set of fuses that limit the load to the ampacity of the tap conductors
Can one interpret this as immediately terminate - not pass thru anything f. e.g. meter
I guess not but I would not like to redo the install.
You guys are professionals.
Thank you and have a wonderful rest of weekend.
Does 240.21 B(2) (2) limit me and I have to have my conductors less than 10 feet?
(2) The tap conductors terminate in a single circuit breaker
or a single set of fuses that limit the load to the ampacity of the tap conductors
Can one interpret this as immediately terminate - not pass thru anything f. e.g. meter
I guess not but I would not like to redo the install.
You guys are professionals.
Thank you and have a wonderful rest of weekend.