Im going to have to replace the service wires from the transformer to this service.
2 of the conduit runs were parallel 3/0 for the 400 amp and 1 conduit for the single run 3/0 for the 200 amp.
Boss feels we can go straight through the trough without making any splices. I feel we would atleast need to bond the neutral(s) in the trough, but
this has also got me thinking this would be like having 2 service drops feeding the same building unless all conductors were spliced phase to phase
at trough then parallel to the 400 amp and single to the 200 amp off of the splice.
2 of the conduit runs were parallel 3/0 for the 400 amp and 1 conduit for the single run 3/0 for the 200 amp.
Boss feels we can go straight through the trough without making any splices. I feel we would atleast need to bond the neutral(s) in the trough, but
this has also got me thinking this would be like having 2 service drops feeding the same building unless all conductors were spliced phase to phase
at trough then parallel to the 400 amp and single to the 200 amp off of the splice.