socal_j
Member
- Location
- Riverside CA
Did a search and couldn't find this particular question asked/answered.
Concrete Encased Electrode Art. 250.52.(A)3 refers to 20ft length of rebar or #4 wire placed horizontally in footing. However, does the 20ft length refer to the dimension of the concrete contact with earth or just the length of rebar/wire? I have seen drawings for a pier footing (24"D x 4ft Deep) require a #4 wire coiled in bottom 20ft long. This does make sense to me. The purpose of the CEE is to provide additional contact with earth, not just coil a wire up and encase it in a small amount of concrete.
If you had a footing that was less than 20ft in length (say a pump pad that was 3'x5'), and it had #4 rebar in it, would this require a CEE?
What if the same size pad had a web of #4 rebar all tied together that was >20' even though direct earth contact wasn't >20'. Does this require a CEE?
If the same pad was 5' x 6' and had a loop of #4 bar around the perimeter that was >20', would this require a CEE?
Concrete Encased Electrode Art. 250.52.(A)3 refers to 20ft length of rebar or #4 wire placed horizontally in footing. However, does the 20ft length refer to the dimension of the concrete contact with earth or just the length of rebar/wire? I have seen drawings for a pier footing (24"D x 4ft Deep) require a #4 wire coiled in bottom 20ft long. This does make sense to me. The purpose of the CEE is to provide additional contact with earth, not just coil a wire up and encase it in a small amount of concrete.
If you had a footing that was less than 20ft in length (say a pump pad that was 3'x5'), and it had #4 rebar in it, would this require a CEE?
What if the same size pad had a web of #4 rebar all tied together that was >20' even though direct earth contact wasn't >20'. Does this require a CEE?
If the same pad was 5' x 6' and had a loop of #4 bar around the perimeter that was >20', would this require a CEE?