Another Voltage Drop Dilemma

Status
Not open for further replies.

Lbartowski

Member
Location
MN
Does the limitation of voltage drop have anything to do with limiting total power consumption? My state has a voltage drop "requirement" listed in the energy code, however we all know it's not a requirement in the NEC (FPN only), so the decision on whether to enforce it is left up to the inspector.

I've had inspectors require us to re-pull 100 amp feeds to unit panels in apartments with as large as #2/0 wire. Then on the next job we're Ok with #1 aluminum.

It is super frustrating because I never know what the inspector will make us do. I'm curious what experience others are having with this and how you deal with it.

Any info is appreciated!
 
I have not worked in any jurisdictions that have a voltage drop requirement. If there were to be one, IMO, they would need to have some formula that attempts to find a reasonable actual load on a circuit, not just the breaker or conductor rating. Just off the top of my head, maybe something like half to 2/3 of the circuit rating,. Or just go off the full rating and allow a relatively high percent drop like 6% or so.

One important thing to note is for many loads, increased voltage drop Will lower the electrical consumption of the circuit
 