Another Voltage Drop Question

Status
Not open for further replies.

U2cy2

Member
Installing a 50A circuit 1500' from 480V distribution panel, will accept a 5% drop. I understand the need to step up the size of the wire to reduce the voltage drop but am having a little bit of trouble wrapping my head around why, in my case, I am running single phase 277V, my wire needs to be (copper) 250 kcmil vs 480V which will require 2/0 ... I'm still dealing with 277V per phase, does the affect of each phase really help reduce the voltage drop that much?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If you're running only two conductors, and there will be a transformer at the load end, it makes all the sense in the world to supply 480v line-to-line instead of 277v line-to-neutral.
 

Ingenieur

Senior Member
Location
Earth
allowable 5% v drop for 480 is 24 vac
allowable 5% v drop for 277 is 14 vac
10/24 x 1.732/2 ~ 36%, hence wire must be much larger

3 ph v drop = 24 = 1.732 x L x R x i
1 ph v drop = 14 = 2 x L x R x I
assuming L and I are the same, R for the 1 ph must be smaller, ie, larger wire
 