Studying for an exam, question is:
Due to voltage drop, a #2 ungrounded conductor must be increased to a 2/0; the original #8 grounding conductor must also be re-sized. What's the size of the new grounding conductor?
a. #8 AWG
b. #6 AWG
c. #4 AWG
d. #3 AWG
The correct answer is listed as d. #3 AWG
From NEC 250.122(B)
Increased in Size.
Where ungrounded conductors are increased in size, equipment grounding conductors, where installed, shall be increased in size proportionately according to the circular mil area of the ungrounded conductors.
I guess that I'm missing something because it looks to me like the correct answer is #4 AWG.
Table 8 Conductor Properties
#2 AWG Circular Mils: 66360
#2/0 AWG Circular Mils: 133100
#8 AWG Circular Mils: 16510
133100/66360 = 2.005
2.005 x 16510 =33114 (Minimum required)
#4 AWG Circular Mils: 41740 (#3 AWG Circular Mils: 52620)
Not sure what I'm doing wrong. Thank you for any help offered.
a. #8 AWG
b. #6 AWG
c. #4 AWG
d. #3 AWG
From NEC 250.122(B)
Increased in Size.