Actual Test Question Multifamily Standard Calc 40 Units , 1000sq ft , 8kw Range , 2.5kw Water Heater , 1200va DW ,600va Disposal, 18a 120v AC NO LAUNDRY Answers are A=1435 ,B=1596, C=1755 ,D=1950 GOOD LUCK
 

bphgravity

Senior Member
Location
Florida
Re: Another Wa State Admin Test Doozy

40 x 1000 x 3 = 120,000
40 x 1500 x 2 = 120,000
Total light = 240,000

First 3000 = 3,000
Next 117,000 @ 35% = 40,950
Remainder 120,000 @ 25% = 30,000
Total Demand = 73,950

Range Column C = 15,0000 + 40,000 = 55,000
Range Column B = 320,000 x 22% = 70,400

Appliances = 2,500 x 40 = 100,000
1,200 x 40 = 48,000
600 x 40 = 24,000
Total Appliance = 172,000

A/C = 18 x 120 x 40 = 86,400

Total Load = 73,950 + 55,000 + 172,000 + 86,400 = 387,350 / 240 = 1,614-amperes

My answer is E, none of the above?

[ March 07, 2005, 07:41 PM: Message edited by: bphgravity ]
 

pipeit

Member
Re: Another Wa State Admin Test Doozy

Bryan in your calculation you forgot to derate appliance load by 75%.when you recalculate with 129,000va for appliances you end up with 344,350 total va /240=1434.79 or 1435 amps. by the way thanks for showing your math because i was not taking into account column c of table 220.19 at all and i have a funny feeling that may be part of my problem finding the right answer.thanks so much!

[ March 07, 2005, 09:47 PM: Message edited by: pipeit ]
 

bphgravity

Senior Member
Location
Florida
Re: Another Wa State Admin Test Doozy

I don't see how you can apply a demand factor to the appliance load. You don't have four of them?
 

kw

Member
Re: Another Wa State Admin Test Doozy

I think you do have more than four. Don't you have 40 dishwashers, 40 disposals, 40 water heaters?
 

dillon3c

Senior Member
Re: Another Wa State Admin Test Doozy

Originally posted by bphgravity:
I don't see how you can apply a demand factor to the appliance load. You don't have four of them?
------>220.53:Appliance demand factor of 75% would apply to this question...

73,950--> General lighting
55,000--> Range
129,000-> 0.75% Appliances: art. 220.53
86,400--> A/C
-----------
344,350 divided by 240= 1434.79

(A) 1435 amperes

[ March 08, 2005, 06:38 AM: Message edited by: dillon3c ]
 

bphgravity

Senior Member
Location
Florida
Re: Another Wa State Admin Test Doozy

Thanks, I was only looking at per unit instead of total on one service... By the way, I know this is for exam preparation but this exact question proves the point that a standard and optional method are unecessary and shoul dbe consolidated to jusr one method.

Per 220.84, the connected load is 818,400 va.

818,400 x 28% = 229,152 / 240 = 955-amperes.

Why would anyone want to use the standard method? The standard method took me about 6 minutes to calculate, and I still screwed it up becausde of all the demands factors permitted for every separate load. This makes no sense. The Optional method took all of 1 minute and its easy. Find the connected load, apply the demand, your done.
 

dillon3c

Senior Member
Re: Another Wa State Admin Test Doozy

-->A Question for the Electrical Instructors out there of this form.
In my above calculation of the Fixed Motor Rated Appliances useing the -(Standard Method)- of Article 220.
Does any of the Instructors out there see anything,or one step missing in my tabulation of this fixed Motor Appliance Calculation..I have returned to classes, and the way it's being taught this calculation would be incomplete.--If my Instructor is correct,then the true answer of this question in Standard Method, is in fact not posted above.And in the WA.State Exam Question,would be wrong..

-Want some Instructor feedback,in catching this error...

----- dillon ----
 

snapco

Member
Re: Another Wa State Admin Test Doozy

I would also be interested in an answer from an instructor as I have worked this same question out and every time came up with 1435 amps per the standard method. Problem is that the State of Washington people who came up with this "new" system of theirs will not let you know what you missed on a test or what you had right. They are also people who do not sign the front side of a paycheck, keep that in mind.
 

dillon3c

Senior Member
Re: Another Wa State Admin Test Doozy

Originally posted by snapco:
I would also be interested in an answer from an instructor as I have worked this same question out and every time came up with 1435 amps per the standard method. Problem is that the State of Washington people who came up with this "new" system of theirs will not let you know what you missed on a test or what you had right. They are also people who do not sign the front side of a paycheck, keep that in mind.
snapco,
I hard to imagine that a testing facillity/ state exam author does not offer, via payment for reimbursement of their time to view the test taken in way of incorrect answers on test.In N.Carolina, the option is offered,via a appointment scheduled and a fee.
 

dillon3c

Senior Member
Re: Another Wa State Admin Test Doozy

This question has been on the table for some time.The problem that I see with this question is on the fixed motor rated appliances.In Wa.State exam for Standard Calculation,needing to applying 220.18(a),doesn't fit into their equation in above multible answers.Correct answer is in fact 1435.72=>1436 amperes

This test question is one ampere shy of correct answer on my calculator.
 

resistance

Senior Member
Location
WA
Re: Another Wa State Admin Test Doozy

to add: We should do something about this! I'm willing to sign my name on any documentation needed to stop this assumed fraud. It's strange that no one can get the correct answer!?

If someone knows the solution, then come forward.

Thanks!

Also, thanks to the people who are postinf answers and questions. This is giving people the opportunity to practice. I've been gathering the questions and working the problems. Yet, I'm on the same boat as most of us.
A=1435 ,B=1596, C=1755 ,D=1950

1000(3)(40)=120000
1500(2)(40)=120000
1500(40) added, because the question said no laundry, but did not say no laundry for ea unit=60000
Total=300000
-3000@ 100%=3000
Remaining 297000 @.35=103950+3000=106950

Range= 55,000 T220.19
H20=100,000(.75)=75000
Dispo=48000(.75)=36000
Dish=24000(.75)=18000
AC 86,400
Total= 270400+106950=377350/240=1572.29 --which doesn't show as an answer

[ March 25, 2005, 07:41 PM: Message edited by: resistance ]
 

resistance

Senior Member
Location
WA
Re: Another Wa State Admin Test Doozy

Ok I see where I went wrong. Yet Dillon and bph-how did you guys get to 73950 for the general lighting load? I can see that you did this:

240000-3000=237000

then you took 117,000@.35
and 120,000@.25 (T220.11)

but how did you come to getting 117000 and 120000???

I also found that adding in the laundry was a mis-read on my half.

Hope to hear from you! Thanks!
 

resistance

Senior Member
Location
WA
Re: Another Wa State Admin Test Doozy

Thanks Dillion!

I see Dillions got this calculation stuff down!

Thanks to all!
 

resistance

Senior Member
Location
WA
Re: Another Wa State Admin Test Doozy

Thanks for the help!

[ April 18, 2005, 02:06 AM: Message edited by: resistance ]
 