brother
Senior Member
Another water heater went out. I am curious as to how the manufacturer wired the heating elements, this is assuming nothing was changed on it over the years, and the name plate is right. The fuses feeding it was too small in my opinion even for the name plate.
But I am not sure how they came up with the 43 amps. on a 30 kw. I can only assume it only operates 3 heating elements, or 4 at most. Since they are 5kw each. What do you think?
5k X 3= 15000 watts. 15000/480= 31.25
31.25 x 1.25= 39.0625
or 4 x 5k= 20,000 watts 20000/480 = 41.66
maybe they took the 41.66 amps and round up to 42 amps. So the name plate says 43. No paper work on it as it has been there for years they tell me. They used onlly 40 amp fuses to supply it. I wouldve at least went with the 50amp, and thats without the 125%. added.
Am I correct in thinking that only 4 heating elements are going at 1 time?