tony_psuee
Senior Member
- Location
- PA/MD
I have always used the derating factors in table 310.15(B)(2)(a) when determining wire size for multiple motors, or two speed motors run in the same conduit. Now, I have another engineer telling me that for motors that are mechanically interlocked from running simultaneously and two speed motors the conductors for each motor or motor winding do not have to be derated because they will not be carrying current at the same time. I can follow the logic but am uncomfortable with it. Looking at the Article and the table it makes no mention of if the conductors are carrying current at the same time or not. Only if you have X number of wires that are intended to carry current (current carrying conductors) they are limited to Y% of full ampacity of that wire size (percent derate). I appreciate any feedback.
Thanks,
Tony