Am I reading this right? There's a 48" hallway and equipment on both sides.
So we have:

48" of total space.
3.5" of equipment on the left side.
8.09" of equipment on the right side.
Under 110.26(A)(3) "Exception No. 3: Meters that are installed in meter sockets shall be permitted to extend beyond the other equipment. The meter socket shall be required to follow the rules of this section."
Which seems to say that the meter side is fine.
But will the left side equipment clearance be OK, as there is just 33.21 inches of clear space before the electrician's back is up against the meters?