Careful everyone. I recently heard about an interesting experience on a school final inspection. Inspector went to test the hood and when he initiated the test, the power did not shut off to under hood appliances. After quick checks of wiring and drawings, it was found that the 20A, 1P breaker feeding the shunt trip main breaker for the under hood equipment panel was off. Yep just that one breaker.
Moral of the story, if you use shunt trip breakers for the under hood equipment shutoff required by code, this is not a fail safe design. This is because the shunt trip needs power to activate and open the breaker.
I have begun using a contactor and letting the micro switch open the circuit (instead of closing it) and shut everything down. Another option would be to use a low voltage trip breakers instead of the shunt trip. Either way, when micro switch opens the circuit the under hood appliances loose power.