As the submitter of a code change to Art 810 in the 2002 NEC regarding antenna grounding, section 810.21 has the requirements. In 810.21F is a laundry list of the acceptable bondwire grounding locations
(F) Electrode. The grounding conductor shall be connected as follows:
(1) To the nearest accessible location on the following:
a. The building or structure grounding electrode system as covered in 250.50
b. The grounded interior metal water piping systems, within 1.52 m (5 ft) from its point of entrance to the building, as covered in 250.52
c. The power service accessible means external to the building, as covered in 250.94
d. The metallic power service raceway
e. The service equipment enclosure, or
f. The grounding electrode conductor or the grounding electrode conductor metal enclosures; or
When you run coax, the rules for coax are in Art 820 and contain similar grounding requirements
Its very important to create for the antenna and coax a single point ground, by running a bond wire to the electrical grounding system, at one point.
If you bond to the electrical breaker room, in a lighting strike, there will be a difference of potential between the antenna, coax, and electrical ground, resulting in current flow, resulting in damage to electronic equipment.
For your distance you may need to increase the size of the bonding jumper.
I bond my antennas with 2 AWG just for physical protection.