Mike Holt said:
An accessible bonding point must be provided at service equipment or the disconnecting means of separate buildings or structures for communications systems. The point can be any one of the following:
(1) An exposed, nonflexible metallic raceway.
(2) An exposed grounding electrode conductor.
(3) An external connection approved by the authority having jurisdiction.
FPN No. 2: Communications systems must be bonded together. Figure 250?134
? Antennas/Satellite Dishes, 810.21
? CATV, 820.100
? Telephone Circuits, 800.100
Author?s Comment: The bonding of all external communications systems to a single point minimizes the possibility of damage to the systems from potential (voltage) differences between the systems.
Amazing, isn't it?michaelr said:61 posts on a green ground screw and nothin' on this?
Just the one's at my home, and that's because I did them.tom baker said:What percentage of the direct digital TV dishes are correctly grounded and bonded? Has anyone ever seen one done per the NEC?
georgestolz said:I believe the answer is that the access point for the LV installer would need to be accessible without opening a high-voltage cabinet.
810.21(F) lists potential bond points quite clearly. Essentially, equipment ground (such as the ground block in the control panel Michael speaks of) is never used as a bond point. The path created by the antenna and lead-in discharge grounding conductor is always taken as directly to earth as electrically possible... and that means never through equipment or an equipment grounding conductor. Though equipment grounding may provide a low impedance path to earth ground, the slight resistance that it does have to the grounding electrode system could elevate bonded equipment enclosures and such to damaging if not fatal voltage levels when an attempt to dissipate thousands of volts is in progress.georgestolz said:Where's the main disconnect for the building? I believe it's supposed to be terminated there.