Does NEC require anti-seize compound to be put on the threads of breaker lugs in an outdoor switch gear?
If you do that and then torque to the specification, you will likely break the breaker.
We do on AL also but this is all copper wire.We used to use corrosion inhibitor on the Al wires, but never anti-seize on the threads
If you do that and then torque to the specification, you will likely break the breaker.
Torque specs for fasteners (nuts on bolts, lug nuts on car wheels, etc.) typically are set to produce the desired linear force on the bearing surfaces assuming the friction of dry threads is contributing to the measured torque.Why do you say that? It will lube the threads allowing you to get there easier but the torque is the torque. Unless you overshoot because it turns so easy. ETA: Or are you saying that the torque spec accounts for dry threads?
To the OP's question, no. It was never required or even recommended to be applied to screw threads, only the AL conductors.
Only exception might be the threads on AL rigid conduit.
-Hal
Yes I am saying that the torque spec is based on dry threads, and putting lubrication on the threads will result in greater contact pressure and may damage the lug and/or conductor.Why do you say that? It will lube the threads allowing you to get there easier but the torque is the torque. Unless you overshoot because it turns so easy. ETA: Or are you saying that the torque spec accounts for dry threads?
To the OP's question, no. It was never required or even recommended to be applied to screw threads, only the AL conductors.
Only exception might be the threads on AL rigid conduit.
-Hal
Torque is torque but the pressure put on the lug and the conductor will be greater if there is less friction in the threads. This is also true when engine building. They will specify torque with and without additives.Why do you say that? It will lube the threads allowing you to get there easier but the torque is the torque. Unless you overshoot because it turns so easy. ETA: Or are you saying that the torque spec accounts for dry threads?
To the OP's question, no. It was never required or even recommended to be applied to screw threads, only the AL conductors.
Only exception might be the threads on AL rigid conduit.
-Hal
Yes I am saying that the torque spec is based on dry threads, and putting lubrication on the threads will result in greater contact pressure and may damage the lug and/or conductor.
Visualize driving a wedge into a tapered slot between two pieces of metal while you measure the clamping force required to hold the two pieces together.That's really hard for me to wrap my head around.
JAP>
Yep, a modified inclined plane, one of the seven basic machines.For this purpose a screw thread is simply a long wedge wrapped in a spiral.
Where you are fastening things together that is true, but I think for wire connections in a lug it is about "compressing" the conductor.Torque is really about fastener stretching.
Where you are fastening things together that is true, but I think for wire connections in a lug it is about "compressing" the conductor.
But the relationship between the elongation and the torque required is still strongly dependent on the thread friction.It is, but depending on the lug design, either the screw or the lug box is in tension. That’s where the stretch comes into play.