cowboyjwc said:For raceways containing ungrounded conductors 4 AWG or larger-yes
JJH said:We have always used anti short bushings when terminating flexible metal conduit "Greenfield", I have been asked if this is a code requirement couldn't find the answer, any input?
ryan_618 said:How does that require an anti short bushing? Are you refering to 300.4(F)? It seems to me that a plastic bushing on a locknut satisfies that rule.
infinity said:Just to be clear an anti-short bushing and a raceway bushing are not the same thing.
cowboyjwc said:They may not be the same thing, but they serve the same purpose.
Pierre C Belarge said:Jim
What would you do if an inspector made you do it?![]()
Jim W in Tampa said:This is such a simple save your own but thing i cant believe any one would not do it.
infinity said:I would disagree. A piece of FMC with #4 conductors in it would require a bushing at the connector. An anti-short bushing inside of the cut end of the raceway wouldn't satisfy the requirement for a bushing.
cowboyjwc said:I'm not arguing that they are different, what I'm saying is, they serve the same purpose. You are not putting that bushing on to protect the conduit.
cowboyjwc said:It is few and far between on ispections that I see a conduit bushing installed prior to the wire being pulled and I have actually let them use an anti-short bushing if the already heated up. Not so much any more as they will never learn if you let them get away with things to often.
cowboyjwc said:Oh then I wasn't wrong. Those are the ones I was talking about. Now doesn't that act like an anti-short bushing?