Anti -Short Bushings
I seem to remember seeing this in one of the forums ,but can not find it now.Is an anti short bushing required on the end of the metal casing? :confused:
gregoryelectricinc
Re: Anti -Short Bushings
If youir talking about type MC cable......yes. There are some fitting manuf.'s that incorporate the anti-short into the fitting for a quick, easy install. I believe Arlington's MC connectors are this way.
joe tedesco
Here is the message by this member:
Joe Tedesco, ECN Member, posted 02-21-2003 03:38 AM
NEMA ENGINEERING DEPARTMENT BULLETIN No. 90
August 14, 2002
Use of Anti-Short Bushings for Terminating Type MC Cable
There has been much confusion within the Installation and Inspection communities regarding the use of anti-short bushings for terminating Type MC cable. The confusion stems from the fact that some MC cable manufacturers include anti-short bushings with their cable.
The inclusion of anti-short bushings with coils or reels of MC cable is based on historical practice relating to the requirements of 320.40 of the NEC, which mandates the use of anti-short bushing or its equivalent protection for Type AC Cable
Fittings used with Type MC Cable are required to be listed per 330.40 of the NEC.
NEMA supports the use of listed fittings for MC Cable. The design of these fittings may or may not include an insulated throat however, they are required to be provided with a smooth, rounded end stop so that the metal sheath of the cable will not pass through and the wires will not be damaged in passing over the end stop.
Whether or not an insulated throat is part of the listed product, these listed MC fittings do not require an additional anti-short bushing. Anti-short bushings that may be supplied by MC Cable manufacturers are for optional use by the installer, however they are not required.
ROP #7-116 from the May 2001 Report on Proposals (ROP) for the 2002 NEC was a proposal seeking to require anti-short bushings on all MC Cable termination installations.
The following is an excerpt from the Panel statement rejecting the proposal:
Anti-short bushings are not required for Type MC cable in accordance with the listing for the product. The termination fittings approved for use with Type MC cables are designed such that the wires will not come in contact with the cut edge of the armor; the throat of the fitting is small enough to prevent contact with the armor. Type MC termination fittings perform the same function for Type MC cable as Type AC terminations plus the anti-short bushing do for Type AC cable.
NEMA supports the uniform adoption and enforcement of the NEC and recommends that local Authorities Having Jurisdiction follow the requirements of NEC Section 330.40, Boxes and Fittings for MC Cable. Section 330.40 requires that the fitting be listed, but does not mandate the use of an anti-short bushing.
www.nema.org
[ August 03, 2003, 10:19 AM: Message edited by: joe tedesco ]