pauls371
Member
- Location
- West Palm Beach Florida
Im working on a job and trying to size the service and feeders for a 6 unit apartment building. The building contains 6 apartments around 1400 sq feet of living space per apartment. Also 6 garages. 208 volt.Im a bit new as to a service of this size but have come up with using code 220.84 Units all have 50 amp stove and 30 amp A/C units
If i apply code 220.84 (C)-1 3 VA for all lighting and all outlets per sq ft 45,000 VA
add in 1500 VA for each 2 wire circuit for appliances. 54,000 VA ....about 6 per apartment
Nameplates of AC units 21,600 VA
Electric stoves at name plate 62,000 VA
i come up with 878 amps
Code says use table 220.84 and for 6 to 7 dwelling units my demand factor percent should be 44%
equals 386 amps
I SHOULD BE GOOD WITH 400 AMP SERVICE i think????
Please if you are familiar could you please review and let me know any thoughts you might have.