It's never been installed but the guy that gave it to me has had it for some time.
![ltVAJgT.jpg](http://i.imgur.com/ltVAJgT.jpg?1)
![4vXAypm.jpg](http://i.imgur.com/4vXAypm.jpg?1)
Service equipment, residential application. Replacing a 100 amp existing panel.
Service equipment, residential application. Replacing a 100 amp existing panel.
Surface mount or flush?
I think i saw 3R in the picture.
If its resi and there is a 100 amp panel there now. My guess is it was flush mounted and most of the circuits came in from the top.
A 3R panel doesnt have holes in the top.
Sent from my SM-G360P using Tapatalk
The label said it had a meter socket, and on the top right of the label it says 3R.
If there is a flush mount panel existing it is most likely behind the meter and he could leave the can and use it as a junction box.
I don't believe there is an expiration date on these units (but I've been wrong before).
Completely all my fault. I without meaning too misunderstood the reason for the question ,,,can I use this panel, without any details as to the application it seemed like , for what and how were missing.
Sent from my SM-G360P using Tapatalk
Because of what the poster I was responding to said.You claim there might be a flush panel behind the meter- Why?
Well, never have been to CA, I would not know that and here on the east coast it used to be a common practice and a service change often involves dealing with it.This is California we generally use Meter / combos. not a meter socket and a panel somewhere else.
How do you install the service entrance conductors if you recess the meter socket?this panel is a semi-flush( thus the F ) and will carry a 3r rating because the cover needs to be rated raintight although it is mounted in the exterior wall . It will have KO's on top as well as below.
Well I'm sure glad you informed me of that. :roll:Many panel upgrades are done with the original panel removed from the wall.
You claim there might be a flush panel behind the meter- Why?
I don't believe he didBecause of what the poster I was responding to said.
you should visit before we fall into the pacific.Well, never have been to CA, I would not know that and here on the east coast it used to be a common practice and a service change often involves dealing with it.
this panel is a semi-flush( thus the F ) and will carry a 3r rating because the cover needs to be rated raintight although it is mounted in the exterior wall . It will have KO's on top as well as below.
How do you install the service entrance conductors if you recess the meter socket?
Usually yesEdit: Does the "U" mean it is designed for an underground fee? If so, POCO would let you "flush" mount that and have their service conductors inside the building?